Just a few of things that can be easily missed when researching Renogy's DC-DC 20/40/60A chargers. It's all in the manual that you can download from Renogy. Feel free to correct my comments if your experience with the units prove otherwise.
#1 - LC connection - that connection is used to limit current. Charging amperage is limited to 12.5% of the rated input for the 20A and 40A models and 50% for the 60A model. The 60A model can function like a 30A model for example.
#2 - Watt rating - that's how you can figure out the max amps in at various voltages.
Max Rated Output Power:
20A model 250 watts ... 250W/20A = 12.5V
40A model 500 watts ... 500W/40A = 12.5V
60A model 750 watts ... 750W/60A = 12.5V
so at 14.4V I'd assume that means:
20A model 250 watts ... 250W/14.4V = 17.36A
40A model 500 watts ... 500W/14.4V = 34.72A
60A model 750 watts ... 750W/14.4V = 52.00A
#3 - Up to 50% greater input amperage needed (copied from manual)
40A model : 40A + 50% = 60A
60A model : 60A + 50% = 90A
-------------------
I've looked at the specifications for several DC/DC units and for the price, I like the Renogy units (North American availability).
If LC (50% current limit) can be triggered on the fly via a switch then I'd probably get the 60A model as it would be an easy way to give the alternator a break if it's running too hot.
Just a few of things that can be easily missed when researching Renogy's DC-DC 20/40/60A chargers. It's all in the manual that you can download from Renogy. Feel free to correct my comments if your experience with the units prove otherwise.
#1 - LC connection - that connection is used to limit current. Charging amperage is limited to 12.5% of the rated input for the 20A and 40A models and 50% for the 60A model. The 60A model can function like a 30A model for example.
#2 - Watt rating - that's how you can figure out the max amps in at various voltages.
Max Rated Output Power:
20A model 250 watts ... 250W/20A = 12.5V
40A model 500 watts ... 500W/40A = 12.5V
60A model 750 watts ... 750W/60A = 12.5V
so at 14.4V I'd assume that means:
20A model 250 watts ... 250W/14.4V = 17.36A
40A model 500 watts ... 500W/14.4V = 34.72A
60A model 750 watts ... 750W/14.4V = 52.00A
#3 - Up to 50% greater input amperage needed (copied from manual)
20A model : 20A + 50% = 30AWhen charging converter is sending full charge, the amperage consumption will be 50% greater on the input side.
40A model : 40A + 50% = 60A
60A model : 60A + 50% = 90A
-------------------
I've looked at the specifications for several DC/DC units and for the price, I like the Renogy units (North American availability).
If LC (50% current limit) can be triggered on the fly via a switch then I'd probably get the 60A model as it would be an easy way to give the alternator a break if it's running too hot.